A contractor had the job of installing in a car wash a rooftop exhaust fan - 480 - 3 ph, 3HP. There was a spare 100 ampere 3ph circ. Brkr. in the dist panel which he used to feed his combination starter. He ran 3/4" RMC and #12 wire to feed the combo starter. The combo starter is properly sized with OL heaters, supply side fuses, control xfmr. fuses, etc...
I have told him that the #12 is undersized and that if he wishes to use that 100 amp CB he needs to pull in the proper size conductors (#2) (and increase conduit size) that could handle the load up to the rating of the OCD.
I am tired of reading Art. 430.
Where can I point to justify my opinion.
Thanks, John