malachi constant
 - Minneapolis
I am feeding a new panel in an existing building. Due to a number of factors that I won't get into here it appears to be cheaper to route the feeder as follows:
1. Feed from fused switch in main panel located inside building.
2. Exit building perimeter, go underground, trench a ways down the building, come back in to same building at different location.
3. Terminate at panel about 30' inside building.
The project manager is on board with this being the ideal solution. However I had another engineer tell me I would need a disconnect at the point where the feeder comes back into the building. I am familiar with needing a disconnect at service entrances, outbuildings, etc, but this is not considered a service entrance as defined by the NEC. I know of no code requirement for a disconnect here. The feeder is protected at the main switchgear, inside the same facility. I don't see how popping outside and coming back in is any different than popping through the foundation and back up - a common practice.
Pretty sure I'm right here. The guy isn't picking a fight, just brought it up as something he thought I had wrong and recommended I double check. Thoughts? Thanks!