Hi All! Long time lurker, first time poster!
I'm trying to figure out if the grounded conductors in the feeder supplying my 208V/120 (3ph,4w) panel would count as a current carrying conductor. The 208V panel has ~20 branch circuits. All of them (except for 1) are 2P circuits and they each feed a 10kVA L2 EV charger. This particular charger has a 208V single phase connection that takes (2) #6 hots and an EGC. No neutral is run to the charger. The last circuit is a 120V circuit to a maintenance receptacle near the equipment.
However, it's my understanding that an EV charger can count as a nonlinear load. In this case, should I count the grounded conductor in the feeder supplying my panel (which is dedicated to EV charging loads) as current carrying? If yes, we'd have to derate the wire in the conduit.
I know that nonlinear harmonics can effect the transformer, but does it also effect the feeders upstream?
I guess the easiest solution would be to stick a CT around that conductor to see how much current is actually flowing and whether or not it contributes enough heat to require derating, but we'd have to actually install it first.
Anyone have any experience with this? Thanks!
I'm trying to figure out if the grounded conductors in the feeder supplying my 208V/120 (3ph,4w) panel would count as a current carrying conductor. The 208V panel has ~20 branch circuits. All of them (except for 1) are 2P circuits and they each feed a 10kVA L2 EV charger. This particular charger has a 208V single phase connection that takes (2) #6 hots and an EGC. No neutral is run to the charger. The last circuit is a 120V circuit to a maintenance receptacle near the equipment.
However, it's my understanding that an EV charger can count as a nonlinear load. In this case, should I count the grounded conductor in the feeder supplying my panel (which is dedicated to EV charging loads) as current carrying? If yes, we'd have to derate the wire in the conduit.
I know that nonlinear harmonics can effect the transformer, but does it also effect the feeders upstream?
I guess the easiest solution would be to stick a CT around that conductor to see how much current is actually flowing and whether or not it contributes enough heat to require derating, but we'd have to actually install it first.
Anyone have any experience with this? Thanks!