That's kind of the road I was going down.
If you put a 208 volt branch circuit and a 120 volt branch circuit in a raceway and utilize all four system conductors it counts as 4 CCC for ampacity adjustment reasons.
Now make it so these are the only loads in the panel. The feeder has same number of conductors, same load on each of the conductors but it only counts as 3 CCC's. See what I'm getting at?
You raise a good point. Although it's not clear to me that the code language draws a distinction between your two examples; it depends on how you interpret the word "circuit."
2017 NEC 310.15(B)(5)(a) says "A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted . . ." Reading this fresh, I have no idea what it is trying to say. In any circuit, with a consistent sense of positive current, the sum of the currents in the circuit conductors will always be zero; otherwise charge would be accumulating in the downstream portion of the circuit. From this point of view, any single conductor always carries only the unbalanced current from all the other circuit conductors, in that if the other circuit conductors currents sum to zero, the conductor current will be zero; and if it not, the conductor current will be the negative of the sum of the other conductor currents.
But clearly 310.15(B)(5)(a) does not intend to exclude the neutral conductor of a 2 wire circuit. I was hoping that the definitions in Article 100 would let us say that a 2 wire circuit does not have a neutral conductor, but a neutral conductor is defined as a circuit conductor that is connected to the source neutral point.
Cheers, Wayne
If we want to be thoroughly legalistic about it, we could say that because the neutral in kwired's feeder doesn't carry the unbalanced current from other conductor
s,
plural, it doesn't qualify for the exemption from being counted as a CCC. It only carries the unbalanced current from one other conductor of the circuit. This also should go some distance to clearing up Wayne's uncertainty about the meaning and clarify why a neutral in a 2-wire circuit is a CCC. When we speak of "unbalanced" current it has to be from more than one conductor that is not a neutral.
(Also, Wayne, I'd say it is not so that "any single conductor always carries only the unbalanced current from all the other circuit conductors". Only a neutral does, kind of by definition and nature. If I have two loads, L1-N and L2-N, on a 4-wire MWBC, L3 does not carry any unbalanced current. Only N does.)
Unfortunately this isn't a wholly satisfying answer, for at least a couple reasons:
- It really give us an unreasonable answer to the OPs question, as winnie explained in post #16.
- If we add a second 120V branch circuit to kwired's example, we still have the same problem that all conductors could carry their max current at the same time, even though the neutral now meets the language of carrying unbalanced current from 'other conductors'.
The intent is clearer than the language. Where the following is true (or close enough) ...
And for good reason. It will carry it's maximum current only when one of the ungrounded conductors is carrying zero current.
then the neutral shouldn't be counted as a CCC. But as we've seen, there are examples where this isn't strictly true for a feeder. What Will said here can only be counted upon for an MWBC that complies with 210.4(C) without using exception 2, i.e. it has line to neutral loads only.