feeder
feeder
Perhaps then the answer is 800 amps, which would mean the neutral is sized the same size as the service conductor.
feeder
IMO, the "more info" makes the question even more confusing...
Again making assumptions, an 800A 480/277V service would require at least parallel 500kcm Cu 75?C conductors for 701A to 760A calculated load, or parallel 600's fro 761 up to 800A calculated load. The minimum neutral service conductor by 250.66 GEC sizes respectively would be 2/0 and 3/0 Cu, neither of which are close to 400, the lowest value answer to choose from.
There has got to be some pertinent info missing
Perhaps then the answer is 800 amps, which would mean the neutral is sized the same size as the service conductor.