I have worked out the following and asking if it right or wrong on how I arrived at the answer-
Calc feeder protective device- using Inverse Time Breaker
240V 3ph delta system
1 15hp 3ph
2 10hp 3hp
1 50hp 3hp 5 min intermitt duty rated
50hp- 130 amps 130x2.5=325 use 350
15hp- 42 amps 42
10hp- 28 amps 28x2=56 56
total 448
a) 300 b) 350 c) 400 d) 450
I came up with answer 'c'-
I figured that the 5min intermitt only was for sizing the conductors and was not used in branch circuit or feeder device calc's
Could anyone advise me if I am right or wrong as I think it is one I missed on a test- thanks