Re: Feeder Protection -WA Admin
Several members have stated that 430.62(A) and its Exception prohibit us from ?rounding up.? They do not. Look at them more carefully.
</font>
But there is more:
</font>
Several members have stated that 430.62(A) and its Exception prohibit us from ?rounding up.? They do not. Look at them more carefully.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">430.62(A) says to start with the highest allowable rating (of the short-circuit device) for the biggest motor, per 430.52.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">430.52 allows rounding up to the next higher size, in certain cases.</font>
But there is more:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Exception 1 to 430.62(A) only comes into play when the circuit breakers are of the instantaneous type. Even so, it does not tell you to ?round down.? What it tells you is that the number you use for the ?highest allowable rating (of the short-circuit device) for the biggest motor? can be no higher than the percentage (from Table 430.52) times the full load current.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Note that in my solution I continued to use the value 325 amps (I did not round it down to the next lower standard value). I finished the calculation by adding in the other three motors. Then I picked the next lower standard value.</font>