That is a very good observation Larry. I also wonder if that design will have to be maintained, 2 runs of 4" conduit.
The required ampacity is 451A. 250kcmil = 290A * 2 sets * 80% adjustment factor = 464A.
You would need 700kcmil to use a single set.
IMO both need to be the same, I would run less than 4 inch if planning to parallel in separate conduits though. If 4 inch is already there, I'd likely increase conductor size as needed instead of adding a second 4 inch.If they go with two conduits, don't the paralleling rules require the second conduit also be 4"?
Copper cost more than steel. both are back breaking labor intensive when you get to the sizes in question here. If you can return the copper you have and only pay difference for one size larger could be least costly overall.I'm going to leave it up to them to determine the most cost effective way. But they already had bought all the 4/0 wire and it has being pulled into the single conduit. To me it seems less costly to add another 4 inch conduit and separate the two pairs instead of exchanging the wire for a 250MCM and run a bigger size conduit to fit. What do you guys think?.
That is a very good observation Larry. I also wonder if that design will have to be maintained, 2 runs of 4" conduit.
I'm not even seeing where they have to be the same material
If the 4/0 can be returned (helps if full reels and no custom cutting) it is probably less cost to do that and get 250 instead.4" EMT should have room for 18 4/0 conductors. The conduit currently has 7 (and the ground might me smaller). Would pulling in an additional 3 4/0 phase conductors be a reasonable pull? Or pulling out the existing, adding 3 more and then pulling in the entire set?
3 sets of 4/0 copper would give a derated ampacity of 546A, so the question is if this is a practical method of correction in this case.
-Jon
If the 4/0 can be returned (helps if full reels and no custom cutting) it is probably less cost to do that and get 250 instead.
Hello everyone. Here is the latest from my electrical contractor. The 4/0 wire that they selected has an insulation rated for 90 C temperature. They are suggesting to do something that I have seen Mike Holt discuss in some of his video series. They want to run 250 Kcmil (2 pair per phase) on a single 4" EMT conduit from the Bus plug to a separate junction box containing a power distribution block with terminals rated for 90 C.
Mike holts discusses on this video, https://www.youtube.com/embed/ItJ0YNOZ4wA, that this setup is a permissible exception to the NEC code. Is this correct or you guys have a different understanding of this possible exception.
So this is completely wrong? That's the solution the electrical contractor is suggesting. Are those the NEC articles, David?
Thank you so much David for that clarification.