Hello rose1981, I think you still have to check it for verification, see attached. Per table the sizes are "based on the rating of the overcurrent protective device." To compensate for voltage drop (more than 100ft), we need to upsize the feeders.
Should I size the cables based on the over current protective device rating as per feeder schedule attached? or do a voltage drop calculation to size the conductors?
If someone gives you a drawing that already has the OCPD and wire sizes on it, why would you think it is your job to change them, unless you are being paid to proof them, other than for obvious mistakes like typos, or undersized wires.
Generally the OCPD size wouldn't change even if the conductor were sized larger for VD compensation.
For example, say you need a 200 amp feeder for a 200 amp panelboard which would typically be #3/0, if you up-sized to 600 kcmil for an extra long distance then the feeder would still be a 200 amp feeder making the OCPD would then be 200 amps. In this example the panelboard is only rated for 200 amps so even though you have larger conductors you cannot exceed the 200 rating of the panelboard.
Because many engineers make drawings or project spec's that have a disclaimer in them putting Code compliance on the contractor. While voltage drop isn't a Code compliance issue, making certain voltage drop will not degrade equipment operation and such is something a conscientious contractor/electrician will do if there are no indications of a comprehensive analysis has been done (IMO).If someone gives you a drawing that already has the OCPD and wire sizes on it, why would you think it is your job to change them, unless you are being paid to proof them, other than for obvious mistakes like typos, or undersized wires.
What I'd like to know is how you know Table 3.75 and the notes thereto are the same on rose1981's project when you are a half a world away???Hello rose1981, I think you still have to check it for verification, see attached. Per table the sizes are "based on the rating of the overcurrent protective device." To compensate for voltage drop (more than 100ft), we need to upsize the feeders.
What I'd like to know is how you know Table 3.75 and the notes thereto are the same on rose1981's project when you are a half a world away???