Is it legal to bring a feeder sized smaller than the rating of the panel it supplies? Example: 100amp mcb-#4 wire feeding 200 amp mlo panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree. Many of the commercial panels we install are fed with 100 amp feeders but the bus is typically rated for 225 amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
mesarush1 said:
Is it legal to bring a feeder sized smaller than the rating of the panel it supplies? Example: 100amp mcb-#4 wire feeding 200 amp mlo panel.

I agree with the others but a #4 with a 100 amp OCP is questionable. If it's a residence then you must abide by art. 310.15(B)(6) and Table 310.15(B)(6).

No romex in this situation and it must be the feeder between the main disco & lighting and appliance branch panelboards.
 