So one normal feed and one EM to the same ATS just about same distance each.
The normal feed has an shunt trip breaker in the run.
The engineer calls for (3) sets of 500's for the normal feed but only (2) sets of 600's for the EM feed. Not sure why different, should be the same right?
Even so the (2) of 600's aren't enough as the fuse size is 1000A.
The normal feed has an shunt trip breaker in the run.
The engineer calls for (3) sets of 500's for the normal feed but only (2) sets of 600's for the EM feed. Not sure why different, should be the same right?
Even so the (2) of 600's aren't enough as the fuse size is 1000A.