ON A 3000A 277/480V SERVICE WE AND THE ENGINEERING COMMUNITY USE 8 SETS OF 4#500 CU WITH
4WIRES PER CONDUIT NOT COUNTING THE NEUTRAL AS A CURRENT CARRYING CONDUCTOR THEREFORE NO DERATING
BASED ON 310.15B4
WE HAVE JUST HAD AN INSPECTOR SAY WE MUST USE 6OO
CU BECAUSE HE IS COUNTING THE NEUTRAL
THE PROJECT IS A TYPICAL MULTIUSE BUILDING WITH
MIXED LTG,MECH LOADS AND XFMRS FOR 120/208VLOADS
IS HE CORRECT