Feeder Size

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Looking at a budget with no feeder sizes. In the instance below. The 800 panel feeding the 200A panels would more than likely never have a feeder sized larger than 200A....out another way the breaker feeder the 200A panel would more than likely not be larger than 200A, correct?

1767802997779.png
 
Assuming that voltage drop is not an issue just go with the code minimum. For 200 amps, #3/0 copper.
 
Top