I am sizeing up a 400 Amp service.400 amp switch, 6 meter/discos w/ a house meter. Can someone explain to me the the words' Individual Dwelling UnitS' as used in 310-15 for my overhead. It seems to me the word 'Individual' cotradicts multi family dwelling.
310.15(6)
For individual dwelling units of one family, two family, and multi family dwellings..................
So I can still use 310.15b(6) table, correct for the service lateral
310.15(6)
For individual dwelling units of one family, two family, and multi family dwellings..................
So I can still use 310.15b(6) table, correct for the service lateral
No, not for a lateral to multiple residences.
It can only be used when the entire load - of only one dwelling - is carried on one set of conductors.
Otherwise use T310.16.
i'm looking for the wires for the 400amp main switch........