bigpapa400lb
A 120/208 3-phase 4-wire feeder supplies a distribution panelboard. The 32,000 VA load supplied by the panelboard is 80% nonlinear, and 100% continuous. What is the minimum required amperage rating, and THW copper conductior size required for this feeder if it passes through a 45 degree C ambient temperature?
My Calculations:
32000/208 x 1.732= 266A x .82 x 80%= 174A 2/0 CU
Answer key says:169A 2/0 CU
My Conductor size is right but the calculation is wrong?
My Calculations: