electro7
Senior Member
- Location
- Northern CA, US
- Occupation
- Electrician, Solar and Electrical Contractor
I am planning on a feeder tap located inbetween the main breaker and the busbar in a switchgear. The load side of the main breaker is field wired with parallel conductors. I wanted to confirm I need to run parallel conductors off the feeder taps to the line side of my fused disconnect, correct?
The main breaker and service is rated for 600A (not exactly sure the size of the parallel conductors off main breaker) and my fuses will be 300A. I am thinking 1/0 copper or 3/0 al parallel conductors to the line side of my fused disconnect from the feeder tap, does this sound right?
The main breaker and service is rated for 600A (not exactly sure the size of the parallel conductors off main breaker) and my fuses will be 300A. I am thinking 1/0 copper or 3/0 al parallel conductors to the line side of my fused disconnect from the feeder tap, does this sound right?