Feeder tap with equal size conductor

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Can I tap off a feeder with the same size conductor as the main feeder from the same Circuit Breaker?


Sent from my iPhone using Tapatalk
 
That would not be a tap as defined in the NEC. It is simply a spice and is permitted. Note, this assumes that the main feeder conductor has an ampacity at least equal to the rating of the feeder OCPD.
 
That would not be a tap as defined in the NEC. It is simply a spice and is permitted. Note, this assumes that the main feeder conductor has an ampacity at least equal to the rating of the feeder OCPD.

Thanks Don