Good afternoon ladies and gentlemen:
My question today is: a 100A main service disconnect is on a pole at a commercial business and feeds 3/0 overhead triplex (for voltage drop)to a shop building. From this triplex, another #2 overhead triplex feeder has been tapped off and goes to a pole with riser and feeds a main lug 100A panel for receptacles for truck block heaters, which I assume is a continuous load. My question is, does this fall under article 225, 230, or 240.21(B)5? And is a main breaker needed at this panel? I believe bonding and a ground rod driven at this panel is required do to no EGC being routed with the triplex, correct? Thanks in advance.
My question today is: a 100A main service disconnect is on a pole at a commercial business and feeds 3/0 overhead triplex (for voltage drop)to a shop building. From this triplex, another #2 overhead triplex feeder has been tapped off and goes to a pole with riser and feeds a main lug 100A panel for receptacles for truck block heaters, which I assume is a continuous load. My question is, does this fall under article 225, 230, or 240.21(B)5? And is a main breaker needed at this panel? I believe bonding and a ground rod driven at this panel is required do to no EGC being routed with the triplex, correct? Thanks in advance.