Feeder taps
mattjglobe
Moorpark, CA
I have a 400A 480V 3 phase panelboard fed from the main switchboard, protected by a 400A breaker. I want to install a new piece of equipment that requires 300A. Can I tap off of the 400A panelboard with a 300A circuit that terminates in a 400A safety switch with 300A fuses to feed the new equipment? The switch would be located next to the 400A panelboard, not more than 10' away.
Feeder tap
Feeder tap
The new equipment will be located in another room, about 80' from the location of the 400A panelboard. I don't know yet if the new equipment has a disconnect. The feeder tap ends at the first fused disconnect, correct? After that, it is a branch circuit or sub-feeder?
A branch circuit is the circuit conductors after the last overcurrent protective device as per definition in the NEC.
The new equipment can be as far away as you like as long as the tap is not over 25 feet, in your case , before it terminates in overcurrent protection rated at the ampacity of the conductors