The NEC prefers to have an EGC doing the fault clearing in the event of a ground fault, this is the fruition of that goal.jmorrow said:does anyone have any info as the whether this actually will change for the 2008 code? and if so the reasoning behind it??
Tell Ray and Ronald to have a look at the FAQ on this topic while they are blowing the dust off their codebooks.
You've got a mixture there. You were wrong for originally bonding the neutral to the EGC of the feeder to the detached structure, but that could have been resolved by removing the bond. Your inspector was incorrect for saying a ground rod can be the only ground, 250.50 requires all grounding electrodes at the structure to be used. He was also incorrect for having you remove the EGC, that makes no sense whatsoever, IMO.wireless36 said:I recently had a similar argument with an inspector. He wanted the ground rod to be the only ground. He told me to disconnect the ground wire from the main to the sub, and not to bond the ground to neutral because that would allow for parallel currents through the ground rod and the neutral. From what I know the installation as it is now is not protected from faults. It is worse off then before inspection! Am I wrong?