Been looking at rules governing wiring of hot tubs. Cust. has a hot tub that requires a 40A circuit with neutral.
Looking at installing a 40A 2P breaker and feeding a self-enclosed GFCI 2P50 to provide the GFCI protection and disconnect. (40A2PGFCI is hard to come by)
Intending on using UF from panel to disconnect/GFCI.
My question would be: is UF allowed to be used (will be outside under mobile home, some exposed to weather).
As I read feeders are required to be in conduit....per 680.25 (2002) In this installation I see no feeder only branch ckt.?
Anyone know the reason for the 6' limit on LFMC or LFNMC to the tub itself?