yesAre the house and garage two separate structures?
yesIf the structures are separate then there is no issue with one feeder going to the house and one to the garage. Are you saying that there is also wiring between the house and the garage
Then wouldn't the additional feeder be allowed under 225.30(D)? ". . . for different uses such as control of outside lightingIf this is for remote control of lighting . . .
Then wouldn't the additional feeder be allowed under 225.30(D)? ". . . for different uses such as control of outside lighting
from multiple locations."
Cheers, Wayne