AC\DC
- Florence,Oregon,Lane
- EC
Hello, doing a bid for a shop that the owner is adding some decent loads. With some possible in future. Ill state all the info then my question.
ALL NEW
Car hoist
10-Hp (FLC 28)
230 volt
Compressor
2-HP (FLC 12)
230 volt
Welder
20 Amp
240 volt
RV With 50/30/20 setup
WHAT IS CURRENTLY ON PANEL
Currently Feeding a HW tank 4500va
General recep and lighting for shop.
Service is out on the yard with one breaker feeding the house and the current 125 amp feeding this shop that is attached to the house.
Trying to find any reduction i can do to make the feeder smaller. Don't seem to many.
So going through 430.24. 125% of Largest FLC plus 100% of the other FLC
430..26 states I can get AHJ allow smaller ampacity for feeder than allowed in 430.24
Would rather not use that if I don't have to.
So for Welder i could not find anything in 630. so take it at 100%
In 551.73 States Not less than 12,000 va for 50 amp then in last sentence states I only use the highest rated receptacle. So I don't have to include the 30 amp or 20 amp.
Then Just 4500va for water heater then 3500 va for general lighting rounded up for easy. So if everything looks good so far, here is my questions
1: I can't use part IV of 220.83 since is does not serve the TOTAL connected load of the Service. Correct. Second guessing my self.
2: I Don't see any reductions beside 430.26
3: will be supplying this for Rv setup. Its just one RV location its rated for 100 amps But i was just debating on reducing that since they are either going to use the 50 or the 30. They don't have the RV yet.
With no reduction It will just be adding everything up and sizing off that.
Then to figure out if current service is sized right for this will follow 220.84 and then add these loads I specified and then I can use optional method.( I don't see this being a problem but would rather be safe)
Thank you guys for any input on this. If i don't get a reply Ill assume I am correct
ALL NEW
Car hoist
10-Hp (FLC 28)
230 volt
Compressor
2-HP (FLC 12)
230 volt
Welder
20 Amp
240 volt