The customer has replaced a 5 HP Air compressor with a 7.5 HP and after wiring it up he wasn't sure why the breaker kept tripping.
He has 2 Air compressors side by side with seperate Disconnect with 2-pole 30a circuit breakers. They are fed with seperate conductors in a 3/4" EMT about 100' between the Main Panel and the disconnects. The DM's are within 3'.
The Main Panel is single phase @ 240v.
The new Air compressor has a service Factor 1.15. and a FLC = 40a
I went through all my calculations and determine that inorder to keep within a 3% Voltage drop and 80% derating of between 4-6 cond. in a conduit that I would need to size my conductors at #6 THHN.
I want to size my Overcurrent Protection.
Are the conductors from the Main Panel considered the feeders and would the disconnect be considered the Branch Circuit?
The original installation had a 2-pole 30a circuit breakers at the panel and a 2-pole 30a CB at the disconnect wired with #10 THHN and the Air compressor lasted 15 years.
Voltage drop of 100' distance in this installation is acceptable but not when include 4 current carrying conductors in the same raceway.
I feel like i'm over thinking this and I should just remove the 1 of the #10 THHN use the other as an equipment ground and pull in 2 #6 THHN and replace the 2-pole 30a breakers with 2-pole 40a Circuit breakers.
Thank you,
Arthur
He has 2 Air compressors side by side with seperate Disconnect with 2-pole 30a circuit breakers. They are fed with seperate conductors in a 3/4" EMT about 100' between the Main Panel and the disconnects. The DM's are within 3'.
The Main Panel is single phase @ 240v.
The new Air compressor has a service Factor 1.15. and a FLC = 40a
I went through all my calculations and determine that inorder to keep within a 3% Voltage drop and 80% derating of between 4-6 cond. in a conduit that I would need to size my conductors at #6 THHN.
I want to size my Overcurrent Protection.
Are the conductors from the Main Panel considered the feeders and would the disconnect be considered the Branch Circuit?
The original installation had a 2-pole 30a circuit breakers at the panel and a 2-pole 30a CB at the disconnect wired with #10 THHN and the Air compressor lasted 15 years.
Voltage drop of 100' distance in this installation is acceptable but not when include 4 current carrying conductors in the same raceway.
I feel like i'm over thinking this and I should just remove the 1 of the #10 THHN use the other as an equipment ground and pull in 2 #6 THHN and replace the 2-pole 30a breakers with 2-pole 40a Circuit breakers.
Thank you,