is it permissible to run a feeder through a strip mall inside the building having it pass through multiple rental suites before terminating in a sub-panel. 
2008 nec
	
		
			
		
		
	
				
			2008 nec
Its allowed but you must have a means to disconnect all sources of supply in a building. Go outside or run under slab, or comply with 225.32
Its allowed but you must have a means to disconnect all sources of supply in a building. Go outside or run under slab, or comply with 225.32
I agree, if each tenant space is considered a separate building.
Not all fire rated walls separate a building into 2 separate buildings.