- Location
- Logan, Utah
Details make all the difference.
I would say you are permitted to supply this load according to 225.30(D).
I agree.
But I also think you must enter the second building and place a service rated disconnect near the existing service or feeder disconnecting means that currently supplies that building.
I could be wrong about needing it placed near the other service or feeder disconnecting means but even if so, it must still have a service rated disconnect near point of entry to the second building. Check with the AHJ.
You don't need to group the feeder disconnect with the service disconnect but the disconnects must be identified in accordance with 225.37.
Chris