2023 NEC
The Code rules for sizing (common troughs) such as auxiliary gutters, 366.22 (A) ,nonmetallic wireways 378.22, and metal wireways, 376.22(A) found therein shall not exceed 20 percent of the cross sectional area of the aforementioned gutter (s).
Example; a 6 x 6 gutter = 36 square inches (length not considered) 36 square inches x 20 % is available for your conductors.
Consult Chapter 9 Table(s) 5 for approximate area in2 of the conductors.
6 x 6 = 36 in2 X 20 % =7.22 for conductor fill for each of the "troughs". Cannot exceed 7.22
Thanks for reading.
Comments and sarcasm accepted.
TX+MASTER#4544