A lot of good comments.I was told to change how I ran my wire for parralel runs of feeders. What's the code requirement for running parralel runs for feeders does the length need to match within 3%?
Sent from my Moto Z (2) using Tapatalk
From another perspective consider that copper resistance has a temperature coefficient of + 0.4%/degree C. Two parallel wires with a length difference of 3% will share current in proportion to their resistance. The shorter one will carry more current, and with enough current, will warm up by about 8C before the resistance and therefore the current is equal in both wires. This 3% length match guideline seems reasonable.
Having all the short wires in one conduit and all the long ones in the other is not much of a concern from a resistance perspective because additional heating from all the short wires bundled together in the same conduit will cause their resistance to go up and their portion of the shared current to go down. Sort of a negative feedback effect.
The inductive effect from the different parallel wire lengths is probably not much concern. The longer wire has more inductance but the shorter wire, with sufficient current will warm up to balance the current to compensate for both resistance and inductance.
EJPHI