This seems alright to me. #2 ser AL running from a main service with 100 amp OCP to distribution/sub panel inside of house, main service riser is #2 AL. carpenter cut in to feeder during demo and cut ground and one hot half way through. So I cut the feeder at the damaged area, pulled it into a 12"x12" box. I spliced onto it with #4 cu ( Polaris connectors ) I should not have to derate the OCP down to 90 amp, based on 215.2(3) Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors. Any body see a reason why this would be a problem ?