How does the exception even look like?NEC 408.2(2):
Other than the required interconnections and control wiring, only those conductors that are intended for termination in a vertical section of a switchboard or switchgear shall be located in that section.
Exception: Conductors shall be permitted to travel horizontally through vertical sections of switchboards and switchgear where such conductors are isolated from busbars by a barrier.
Might be NEC 408.3 in some code versions.
Probably something custom in this case. Would need something like GPO-3 sheets to separate the wires from the bus. Could be worth reaching out to a federal Pacific rep, if they even exist anymore.How does the exception even look like?
So I am guessing this switchboard is not up to current code