I just ran into an interesting issue with an engineer. There are requirements in a 140' run of 2-1/2" conduit with 4-4/0 XHHW to have a flexible connection at each end. From a J-box with distribution blocks we exit the bottom, 90 degree bend to a 45 degree offset and connect to sealtite with a straight connector. The engineer is directing us to install a sealtite 90 degree flex connection in the end of a 120' run of GRC.
At the other end of the run we are to make a connection from the end of the GRC with a straight sealtite connection and create a drip loop from the horizontal conduit run. This end will have about 270 degree of bend in the sealtite and will terminate in the bottom of another J-box with distribution blocks. \
So I sent the engineer information stating this installation is a code violation:
1. 300-18 Raceway systems must be installed complete prior to pulling conductors, noting the exection which does not apply in this case due to the sealtite 90 is in midspan of the raceway system and not at an end.
2. Chapter 9, 1 and 2 clearly indentify the radius of bends and offer jamming ratio for conductors.
The response I received back was that there is no code violation and you can put a sealtite 90 degree fitting midspan of a raceway system. I have also been told this engineer has the support of DOT engineers.
I have been in this industry for 35 years, I cannot imagine pulling these feeders through 495 degree of bends or trying to pull through a midspan sealtite 90. It goes without saying that I have not proceeded, but I have to ask. Has anyone else run into an issue of being directed to perform this type of installation? I now I'm getting a little set in my way of doing things. However is it allowed to install a seatite 90 mdispan of a feeder run? i my mind this would be the same as putting in a 90 degree plumbing ell. All of the work is exsposed.
At the other end of the run we are to make a connection from the end of the GRC with a straight sealtite connection and create a drip loop from the horizontal conduit run. This end will have about 270 degree of bend in the sealtite and will terminate in the bottom of another J-box with distribution blocks. \
So I sent the engineer information stating this installation is a code violation:
1. 300-18 Raceway systems must be installed complete prior to pulling conductors, noting the exection which does not apply in this case due to the sealtite 90 is in midspan of the raceway system and not at an end.
2. Chapter 9, 1 and 2 clearly indentify the radius of bends and offer jamming ratio for conductors.
The response I received back was that there is no code violation and you can put a sealtite 90 degree fitting midspan of a raceway system. I have also been told this engineer has the support of DOT engineers.
I have been in this industry for 35 years, I cannot imagine pulling these feeders through 495 degree of bends or trying to pull through a midspan sealtite 90. It goes without saying that I have not proceeded, but I have to ask. Has anyone else run into an issue of being directed to perform this type of installation? I now I'm getting a little set in my way of doing things. However is it allowed to install a seatite 90 mdispan of a feeder run? i my mind this would be the same as putting in a 90 degree plumbing ell. All of the work is exsposed.