If I have FEEDERS inside building and they are concrete encased then are they considered outside? What code section? Note I mean Feeders Not Service conductors.
See 225.32
YesHowever I dont follow how you see 225.32 in combo with 230.6 says if feeders are concrete encased then they are considered outside?
This wouldn't happen to be another situation where you have feeders running through unrelated units to get to where they are going and the requirement for outside disconnects?
-Hal
But I wouldn't say that pouring concrete around feeders automatically makes them outside unless they are under a poured floor in the dirt. Neither would running feeders through an interior planting space with some dirt necessarily make it a buried feeder.
.
I see 230.6 as a way out of 230.3 which disallows feeding one building through the interior of another. In that case, you can consider 2" concrete encasement as not being inside the building. Similarly, 225.32 lets you use the concrete encasement rules of 230.6 to allow the disconnect to be further within a building because it isn't inside until the concrete encasement disappears.
What are you trying to do? For the purposes of the required disconnect for a feeder serving a separate structure, 230.6 may be used.??? I still dont follow
What are you trying to do? For the purposes of the required disconnect for a feeder serving a separate structure, 230.6 may be used.
Why would you need it to be considered outside the building?I have feeder inside building that is concrete encased. Trying to see what code says its outside
Why would you need it to be considered outside the building?
No Code says it's outside. But I still don't follow why you would even care.I dont follow. Any conductors routed inside the building are inside normally but then code amends that for service conductors. Code is different. I dont know what code says if feeders are inside building concrete encased are they considered outside or not
No Code says it's outside. But I still don't follow why you would even care.
I dont follow. Any conductors routed inside the building are inside normally but then code amends that for service conductors. Code is different. I dont know what code says if feeders are inside building concrete encased are they considered outside or not
Didn't you ask about feeders?The its in your response what is it referring to service conductors or feeders?
Didn't you ask about feeders?
225.32 does say "for the purposes of this section" which is the required disconnecting means. Only other reason I can think of why someone would want a feeder considered outside is for use of the outside unlimited tap rule. But code says 230.6 applies there too.No Code says it's outside. But I still don't follow why you would even care.