this is for a single family residential home. single phase, 120/240v.
upgrading service to 400 amp. Due to layout, panels can not be near meter location so we will need to install a disconnect next to the meter.
there will be (2) 200 amp panels. one panel in the basement and one panel on the top floor. typically this is not an issue. simply install (2) 200 amp disconnects next to the meter and take one 200 amp feeder to each panel from its own disconnect.
in this case however there is not enough room to install (2) separate disconnects. The only product i see that is narrow enough is a 400 amp breaker enclosure. the 400 amp breaker has 2 lugs per pole.
my question: Is it permissible to take 2 loads to sperate panels on different floors from the load side of one service disconnect breaker?