FEEDING 400aASECTION

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
HI,
WHY SOME ENGINEERS FEED THE 400A METER SECTION BY @500 MCM, THHN,CU @ 75DEG @ 120/208, 3 PH.

AND SOME USE #600 MCM THHN, CU @ 75DEG ?????

AMPACITY OF 500 MCM, THHN, CU @ 75 DEG IS 380A

TANX
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the load is 380 amps or less then you can go up to the next standard size OCPD which is 400 amps. Please turn off the Caps lock. ;)
 
Status
Not open for further replies.
Top