FEEDING 400aASECTION

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
HI,
WHY SOME ENGINEERS FEED THE 400A METER SECTION BY @500 MCM, THHN,CU @ 75DEG @ 120/208, 3 PH.

AND SOME USE #600 MCM THHN, CU @ 75DEG ?????

AMPACITY OF 500 MCM, THHN, CU @ 75 DEG IS 380A

TANX
 
If the load is 380 amps or less then you can go up to the next standard size OCPD which is 400 amps. Please turn off the Caps lock. ;)
 