Questions regarding feeding these (2) pieces of equipment.

According to the legend they are asking for (2) separate conduit runs.

If pricing would you price it this way?

In the field would you run ONE conduit with both circuits to the units then branch of and feed individually?

** Yes, I know when they say conduit it's STUPID..
 
Combining them into one raceway often saves money so it's done all of the time. You'll just need to do a calculation for more than 3 CCC's in the raceway and adjust the conductor size accordingly.
 
Combining them into one raceway often saves money so it's done all of the time. You'll just need to do a calculation for more than 3 CCC's in the raceway and adjust the conductor size accordingly.
Absolutely but could you get hung out to dry if submitting as builts?
 
Do your as-builts include all the conduit runs to each piece of equipment?
 
That’s my point . If we show as builts that differ from the contract drawings then what?
Honestly in my experience no one is checking. So as long as the conductors are properly sized the installation will be code compliant and no one will care.
 
A lot of time there is a general note stating runs can be combined. I find it a lot by the legend for the circuit indicator. If not ask, most will say sure as long as you adjust to be code compliant.
 
That’s my point . If we show as builts that differ from the contract drawings then what?
They can argue that you should have gotten the change from the plans approved before proceeding.

Another option is a single feeder to a sub-panel, with separate conduits from there to the equipment.
 
If the drawings ask for two conduits and you run a single one, and your contract says you will install per the drawings you are in violation of the contract you signed.