Feeding lovo lights

Status
Not open for further replies.

george t. everett

Senior Member
Location
New York
Would it be code compliant to use SPT cable in 3/8" flexible metal conduit (FMC) to feed low voltage undercabinet lights? Still trying to find a better way then using NM solid.
 
Re: Feeding lovo lights

No that would not make it, SPT cord is under article 400 and is not for use in raceways.

14 or 12 AWG stranded conductors in 3/8" FMC would.
 