G george t. everett Senior Member Location New York Jan 28, 2004 #1 Would it be code compliant to use SPT cable in 3/8" flexible metal conduit (FMC) to feed low voltage undercabinet lights? Still trying to find a better way then using NM solid.
Would it be code compliant to use SPT cable in 3/8" flexible metal conduit (FMC) to feed low voltage undercabinet lights? Still trying to find a better way then using NM solid.
iwire Moderator Staff member Location Massachusetts Jan 28, 2004 #2 Re: Feeding lovo lights No that would not make it, SPT cord is under article 400 and is not for use in raceways. 14 or 12 AWG stranded conductors in 3/8" FMC would.
Re: Feeding lovo lights No that would not make it, SPT cord is under article 400 and is not for use in raceways. 14 or 12 AWG stranded conductors in 3/8" FMC would.