Is it legal to strap/run an electrical conduit on a chain link fence framework? We have a few differing opinions in the shop, wanted to see more.
Is it legal to strap/run an electrical conduit on a chain link fence framework? We have a few differing opinions in the shop, wanted to see more.
Is it legal to strap/run an electrical conduit on a chain link fence framework? We have a few differing opinions in the shop, wanted to see more.
As long as you secured the conduit to the poles I think it would be fine.
I am less sure about it if you tried to secure it to the chain link part.
NEC 225.22 What type of raceway are you installing on the fence?
There is PVC there now, that would eliminate any grounding issues of the raceway. I couldn't find anything definitive to prohibit it either.
I would not accept the fence fabric as a conduit support, and unless you are running large size PVC, the support posts are probably at a greater spacing than shown in Table 352.30.There is PVC there now, that would eliminate any grounding issues of the raceway. I couldn't find anything definitive to prohibit it either.
I would not accept the fence fabric as a conduit support, and unless you are running large size PVC, the support posts are probably at a greater spacing than shown in Table 352.30.
Just the AHJ's opinion that the fence fabric is not a suitable support....remember everything has to be "approved".Why not? What code section would preclude using the chainlink itself as a support?
Also, would a chainlink fence that supports a conduit need to be grounded back to the service? If it were building steel, it would be grounded, yes? I seem to recall needing fencing bonded/grounded, perhaps that was around substations, or maybe I am remembering completely wrong. :?
As far as I know zip ties are only suitable for securing and supporting flexible wiring methods.I recently installed a 1.25" PVC conduit run about 100' long on a chain link fence. I fastened it with zip ties to the fence fabric. I made sure it was at least 12" off the ground to avoid physical damage from mowers and put a liquidtight 90 on each end for expansion. The inspector passed it.
As far as I know zip ties are only suitable for securing and supporting flexible wiring methods.
Someone's preference does not make for a code requirement, although I must admit I am not real thrilled with the idea of using the fence fabric itself to support the conduit or using tie wraps to support conduit.Code reference please.
Approved. Acceptable to the authority having jurisdiction.
I must admit I am not real thrilled with the idea of using the fence fabric itself to support the conduit or using tie wraps to support conduit.
The inspector just is not the AHJ
Someone's preference does not make for a code requirement
Why not? What code section would preclude using the chainlink itself as a support?
300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place. .....
They are very strong. I believe I have seen them used as handcuffs when rounding up large groups of criminals.
Not sure how it is in the rest of the world, but the chief inspector here is the AHJ.