This has been going on 2 years.
Usually in the evening a random selection of single pole breakers will trip simultaneously.
I checked all of the neutrals, cleaned the connection in the neutral bus bar where 2 pieces join and added some sheet metal screws to replace the screw that holds it to the panel right below the utility connection (things were good for 6 months after this). Last week I replaced the screw that joins the 2 sections of neutral bus with a bigger longer self tapper since the original had finally stripped out from triple checking it 100 times. Breakers tripped that night.
Residential millbank 200a house panel. Passthrough 100amp breaker to 100amp main subpanel. Neutral for 100a main subpanel connects directly below utility connection and neutral bar is past that. RV breaker (not used) and garage subpanel breakers in meter panel also (garage is barely used and basically has no load if the lights aren't on), plus maybe a hot water heater.
Neutral wire to 100amp subpanel 30ft away is probably 2/0 aluminum. Ground wire to subpanel is probably #4.
Neutral and ground are joined in the meter panel and not in the subpanel. Neutral bar etc. are definitely getting good connection through the meter panel to ground.
Ground bar has 3 good screws going into the panel.
We replaced the ground wire and added a second ground rod last week since resistance was a little high. At the same time all neutral connections were tightened etc. since I sent a new person to go figure it out and start at the beginning and assume nobody had done anything yet. Single pole breakers tripped the next evening randomly.
This house was gutted and we rewired the majority of it 2 years ago and this has been going on since then. New main subpanel and breakers inside with almost all new wire.
There should be no shared neutrals or neutrals touching ground. There are no events that cause the breakers to trip. Only 2 people live there and it will happen while they are sleeping. Usually at night or in the afternoon not during they day when they are using things.
There was one eaton 20a normal breaker, one eaton 20a gfci breaker, and the rest were eaton afci breakers (green ones).
Yesterday we swapped out 2 of the afci breakers with new ones (same kind). We also eliminated a few on lighting circuits and put in non-afci breakers to test things out. So 7 breakers tripped twice at 10pm last night. Mostly afci but also a normal single pole breaker, afci on both legs, all single pole 20a.
The 2 pole breakers have never tripped.
I had the power company out there today and load test the feed with a superbeast and he said it is all fine. He didn't want to test it but he did. It is a bit windy and I asked him to shake the lines a bit too while he was there but I doubt he did since he did a visual inspection when he pulled up.
I am just throwing time and money at this and getting absolutely nowhere.
Usually in the evening a random selection of single pole breakers will trip simultaneously.
I checked all of the neutrals, cleaned the connection in the neutral bus bar where 2 pieces join and added some sheet metal screws to replace the screw that holds it to the panel right below the utility connection (things were good for 6 months after this). Last week I replaced the screw that joins the 2 sections of neutral bus with a bigger longer self tapper since the original had finally stripped out from triple checking it 100 times. Breakers tripped that night.
Residential millbank 200a house panel. Passthrough 100amp breaker to 100amp main subpanel. Neutral for 100a main subpanel connects directly below utility connection and neutral bar is past that. RV breaker (not used) and garage subpanel breakers in meter panel also (garage is barely used and basically has no load if the lights aren't on), plus maybe a hot water heater.
Neutral wire to 100amp subpanel 30ft away is probably 2/0 aluminum. Ground wire to subpanel is probably #4.
Neutral and ground are joined in the meter panel and not in the subpanel. Neutral bar etc. are definitely getting good connection through the meter panel to ground.
Ground bar has 3 good screws going into the panel.
We replaced the ground wire and added a second ground rod last week since resistance was a little high. At the same time all neutral connections were tightened etc. since I sent a new person to go figure it out and start at the beginning and assume nobody had done anything yet. Single pole breakers tripped the next evening randomly.
This house was gutted and we rewired the majority of it 2 years ago and this has been going on since then. New main subpanel and breakers inside with almost all new wire.
There should be no shared neutrals or neutrals touching ground. There are no events that cause the breakers to trip. Only 2 people live there and it will happen while they are sleeping. Usually at night or in the afternoon not during they day when they are using things.
There was one eaton 20a normal breaker, one eaton 20a gfci breaker, and the rest were eaton afci breakers (green ones).
Yesterday we swapped out 2 of the afci breakers with new ones (same kind). We also eliminated a few on lighting circuits and put in non-afci breakers to test things out. So 7 breakers tripped twice at 10pm last night. Mostly afci but also a normal single pole breaker, afci on both legs, all single pole 20a.
The 2 pole breakers have never tripped.
I had the power company out there today and load test the feed with a superbeast and he said it is all fine. He didn't want to test it but he did. It is a bit windy and I asked him to shake the lines a bit too while he was there but I doubt he did since he did a visual inspection when he pulled up.
I am just throwing time and money at this and getting absolutely nowhere.