Fiber optic raceway in a boiler room

Status
Not open for further replies.

nickvoltage

New member
Location
Colorado
Can you run any type of interduct thru a boiler room PVC, Plenum rated and thru the floor in the same room? Or does it need to be EMT? Running fiber optic cable thru it. Thanks Nick.
 

Smart $

Esteemed Member
Location
Ohio
Can you run any type of interduct thru a boiler room PVC, Plenum rated and thru the floor in the same room? Or does it need to be EMT? Running fiber optic cable thru it. Thanks Nick.
Welcome :thumbsup:

Your description needs clarification... but FWIW, the "innerduct" must be listed. You should look at 770.12 and 770.154 before clarifying... though afterwards you may not need to clarify :p
 