Fiber optic run with conductors NON building

Status
Not open for further replies.
art 770 *2005 NEC (*California) refers to NON-conductive fiber optic cable being allowed in shared raceway with electrical power & light conductors under 600V.

this falls under category III. Cables withIN buildings. 770.133

My application would be in existing raceway run throughout a container yard. All conduits are underground outside of any buildings. Can I deduce that art 770.133 still holds true for cables outside of buildings?

I could not find anything in art 770 that referenced installations other than inside buildings. Unless you consider a class I area could be outside of a building. Does anyone know what requirements there are for non building Fiber optic cable installations along side electrical conductors?



FYI- trenching and/or saw cutting (pavement cable) are not an option as there are enviromental concerns. We are looking to install the non-conductive fiber in existing underground lighting power conduits to each of the site light poles. The fiber will be used for tracking equipment mounted up on the site light poles.
 
Take a look at 770.12(A).

any type of listed raceway!!!! OK I guess that is all encompassing enough for me. Of course I still need to follow fill requirements. If it was a snake it would have....


Thank You
 
another issue-

III. cables within buildings
770.133(a) "nonconductive fiber..not permitted to occupy the same cabinet...housing electrical terminations...

common sense would dictate most AHJ's would say that if this is required inside a building then it would also be required outside on a light pole.
 