Field Connections Buck-Boost Transformers

Status
Not open for further replies.

CharleyVA

Member
Need some help doing the connections for a Buck-Boost Transformer. I have a wiring diagram for the connections but frankly cannot understand the diagram.

I need to convert the feed 120 volt, 60 hertz, single phase to 12 volt - low voltage.

The transformer has wires marked H1, H2, H3, H4 and X1, X2, X3, X4

I have a live feed with Black, white and ground and the same for the output lines to the low voltage under-cabinet lights.

Can anyone help me figure out how to make the connections?
 

iwire

Moderator
Staff member
Location
Massachusetts
What are the primary and secondary voltages listed on the trans.

Even better if you give use the make and model number.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
080705-1435 EST

CharleyVA:

Are you really talking about a buck or boost function, or a stepdown transformer with isolation between primary and secondary.

It appears you want a 12 AC output, from a 120 AC input. Is that correct?

.
 

Smart $

Esteemed Member
Location
Ohio
CharleyVA said:
240/120 Primary
12/24 secondary
H1, H3 to 120V supply Black
H2, H4 to 120V supply White
X1, X3 to 12V load Black
X2, X4 to 12V load White
Ground to Ground
 
Last edited:

Smart $

Esteemed Member
Location
Ohio
I should add that the connections I posted above are for standard marked xfmrs. IIRC, some manufacturers of small xfmrs flop H2/H3 and X2/X3 terminations.
 

CharleyVA

Member
Hey Guys - I wanna thank you all for your help - followed your directions, flipped the breaker and everything lit up like a Christmas Tree without a single spark !! Thanks loads!!

Charlie
 