Field made conduit entry into load center

Merry Christmas

voltairzap

Member
Location
Sonoma CA
Occupation
Electrical Contractor
What does this mean? Half of a factory KO is still intact? So what's the issue not a good enough bonding surface? If so then just add a bonding bushing.
There is a bonding bushing at the load center side and a service hub at the meter socket enclosure.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with the others however I have been failed in the past for making custom K/O's for service conductors with too tight of a bend in the wires, it was not the K/O it was wire bending space at the main breaker, when I asked the inspector the cited code section was 312.6
Isn't that section applicable for the wire bending space at the terminal not where the conduit enters the enclosure?
 

voltairzap

Member
Location
Sonoma CA
Occupation
Electrical Contractor
Isn't that section applicable for the wire bending space at the terminal not where the conduit enters the enclosure?
I agree with the others however I have been failed in the past for making custom K/O's for service conductors with too tight of a bend in the wires, it was not the K/O it was wire bending space at the main breaker, when I asked the inspector the cited code section was 312.6.
Basically I failed to consider wire bending space when I made the custom KO.
Another time I had a an issue was a NEMA 4X, they did not allow a KO in the top.
As long as wire bending space is met make holes as needed.
Wire bend radius is not an issue here.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
My question exactly. As AHJ the inspector should be able to make a determination on the installation.
I would like to find a Code section that addresses field cut penetrations, so the inspector can move forward on this.
You won't find any applicable NEC section to your original question which is can you make your own KOs in a cabinet. The answer is yes because there is no prohibition in the NEC if you want to make your own KOs.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As I said, I think 110.2 would be the code section he could cite. Many would say 110.3(b) manufacturers instructions, but they would have to say you CANNOT drill new KO's, they don't have to GIVE YOU PERMISSION to cut new KO's.
I would love to manufacturers instructions for a panel that say you cannot punch your own KO's.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
This is not the first time this has come up here:

Conclusions are the same, I'm just pointing out that this issue with AHJs is not unheard of. I have had similar discussions with a couple of AHJs regarding punching holes in ANY enclosure, as to it "violating the UL listing of the enclosure". UL had available, at one time, a response letter that explained that once a hole is made, whatever goes INTO that hole must have the same or HIGHER level of environmental protection as the original enclosure rating (I can't find that any longer). So if a panel is rated for indoor use, i.e. Type 1, then pretty much any penetration that restores that to Type 1 is fine. Now IF the panel is outdoors, Type 3R, then any penetration must use a "Wet Location" rated connection method, i.e. Myers Hub for example. That is actually codified in 312.2, and repeated specifically FOR PANELBOARDS in 408.16. So if this was a 3R panel, punching a hole and not using a conduit connector method equal to or greater than the enclosure rating might be an issue.
 

voltairzap

Member
Location
Sonoma CA
Occupation
Electrical Contractor
My question exactly. As AHJ the inspector should be able to make a determination on the installation.
I would like to find a Code section that addresses field cut penetrations, so the inspector can move forward on this.

This is not the first time this has come up here:

Conclusions are the same, I'm just pointing out that this issue with AHJs is not unheard of. I have had similar discussions with a couple of AHJs regarding punching holes in ANY enclosure, as to it "violating the UL listing of the enclosure". UL had available, at one time, a response letter that explained that once a hole is made, whatever goes INTO that hole must have the same or HIGHER level of environmental protection as the original enclosure rating (I can't find that any longer). So if a panel is rated for indoor use, i.e. Type 1, then pretty much any penetration that restores that to Type 1 is fine. Now IF the panel is outdoors, Type 3R, then any penetration must use a "Wet Location" rated connection method, i.e. Myers Hub for example. That is actually codified in 312.2, and repeated specifically FOR PANELBOARDS in 408.16. So if this was a 3R panel, punching a hole and not using a conduit connector method equal to or greater than the enclosure rating might be an issue.
So, there is no definitive directive for guidance for the AHJ for field cut KOs?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
So, there is no definitive directive for guidance for the AHJ for field cut KOs?
Well, it's kind of the other way around. There is nothing saying you cannot punch holes in the field. If we all waited to find things in the NEC saying what we COULD do, the world would come to a grinding halt...
 
So, there is no definitive directive for guidance for the AHJ for field cut KOs?
What Jraef said. You don't need permission to punch KO's. There are certainly requirements in the NEC (that vary a little bit depending on if we were talking about an article 312, 314, or 376 item) that might require fittings rated for wet locations. I am assuming this inspector is thinking something along the lines of " if it comes with factory Kos then you can only use those Kos they provide". There is nothing in the NEC or in any manufacturers instructions I have ever seen that states that. As I said before, the only possible thing he could cite is 110.2 just saying that he does not find it acceptable, in which place he is clearly an idiot, has no business being in his position, is wasting everyone's time on silly things when there are much more important things he could be focusing on, and should be fired immediately.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
As I understand it a piece of equipment like a panel board or load center is listed as it is when it comes from the factory so even if you knock out a pre-formed ko instead of making your own hole you are "violating" the listing.
I though the listing doesn't include the enclosure and just covers the guts.

Cheers, Wayne
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I though the listing doesn't include the enclosure and just covers the guts.

Cheers, Wayne
You may be correct. I don't know and I won't spend the energy to find out until I have my own battle to fight. I don't spend too much time worrying about UL listings and when people start telling me I shouldn't do something because it will "violate the UL listing" I put them in the mental file of people who don't know what they are talking about.
 