How many #10 THHN's (stranded) can you legally install in a 2" RMC nipple?
96Originally posted by georgestolz:
How many #10 THHN's (stranded) can you legally install in a 2" RMC nipple?
In other words, if he installed 97 then he would be in violation by 0.80568720379146919431279620853 conductor?Originally posted by iwire:
Well you can fit a little more than 96.
96.919431279620853080568720379147
Do you have .919431279620853080568720379147 of a conductor?![]()
Cool Don, I was not aware of that, so the number is 97.Originally posted by don_resqcapt19:
Look at Chapter 9, Table 1, Note 7.
Originally posted by iwire:
Somebody set us up the bomb or as is commonly known "All your base are belong to us"I wonder if George just set us up on that one.![]()
Sure; just give me a pair of Kleins and 10 minutes per foot, or a hammer and 1 minute per foot.Originally posted by iwire:
Do you have .919431279620853080568720379147 of a conductor?
Originally posted by iwire:
I wonder if George just set us up on that one.![]()
Darn,Originally posted by georgestolz:
How many #10 THHN's (stranded)