fill question

Status
Not open for further replies.
Re: fill question

Well you can fit a little more than 96.

96.919431279620853080568720379147

Do you have .919431279620853080568720379147 of a conductor? :p
 
Re: fill question

Originally posted by iwire:
Well you can fit a little more than 96.

96.919431279620853080568720379147

Do you have .919431279620853080568720379147 of a conductor? :p
In other words, if he installed 97 then he would be in violation by 0.80568720379146919431279620853 conductor? :cool:
 
Re: fill question

Originally posted by don_resqcapt19:
Look at Chapter 9, Table 1, Note 7.
Cool Don, I was not aware of that, so the number is 97.

I wonder if George just set us up on that one. :D
 
Re: fill question

Originally posted by iwire:
Do you have .919431279620853080568720379147 of a conductor?
Sure; just give me a pair of Kleins and 10 minutes per foot, or a hammer and 1 minute per foot.
 
Re: fill question

Oh, I forgot to mention that, after the "adjustment", the conductor will be 1.0876288659793814432989690721649 times as long as it was before.
 
Status
Not open for further replies.
Top