How do you check for ground loops?
My 94 YO neighbor died in August, his wife called today that bathroom outlet was not working. I do mostly airplane power systems, not residential.
30 YO GFCI in garage was tripping, immediately upon reset. Weird way house got wired (1985) via GFCI in garage, 50 ft from bath. GFCI outlet, not breaker.
No 'detectable' leakage current with 6A clamp on.
New GFCI, works ok, so figured bad GFCI after 30 years, no problems till yesterday. Checked known outlets what were dead, all clear in the boxes, nothing plugged in, no known lights on the circuit.
Putting all cover plates back on, hear gas furnace come on. 30 seconds later hear the new GFCI click open. Furnace off, no problem.
So, OK, now need to find where the original electrician crossed some white wires.
Any residential tricks for this? Other than opening up boxes and tracing white wires?
Expect a white wire voltage drop on furnace line (different breaker) is resulting in parallel path WW leakage > 6 mA thru the GFCI thru one of the 2 white wires on the GFCI output which has a > 6 mA parallel current.
I do have accurate enough meters to detect 4 mA current when no direct loads on GFCI outlet lines so at least can isolate which of the 2 white wires are involved on the load side of GFCI, but would think that type current would be >> 6 mA, possibly just capacitively coupled wire to wire, but all is NM, no multiple white wires in same conduit or anything. I have no idea if a bunch of NM all go thru the same stud holes though. The GFCI trip was not just at Furnace start, anytime it was on; Say 2 v drop on white wire to furnace, mA trip of GFCI would need 90 uF or so -- possible that motor start cap in furnace is involved? There is an 240 Vac A/C (off) that has about that value motor run cap on the compressor, probably need to check the white wire to that location also.
I'm assuming the old GFCI did not trip for say 6 mA, with age got 'more sensitive?' BTW, the old one checks ok by itself on a different individual circuit, did not measure the trip limits, but 2 kohm resistor trips it.
Am I missing anything? Any neat tricks for checking?
Whatever it is has been there for 30+ years.
My 94 YO neighbor died in August, his wife called today that bathroom outlet was not working. I do mostly airplane power systems, not residential.
30 YO GFCI in garage was tripping, immediately upon reset. Weird way house got wired (1985) via GFCI in garage, 50 ft from bath. GFCI outlet, not breaker.
No 'detectable' leakage current with 6A clamp on.
New GFCI, works ok, so figured bad GFCI after 30 years, no problems till yesterday. Checked known outlets what were dead, all clear in the boxes, nothing plugged in, no known lights on the circuit.
Putting all cover plates back on, hear gas furnace come on. 30 seconds later hear the new GFCI click open. Furnace off, no problem.
So, OK, now need to find where the original electrician crossed some white wires.
Any residential tricks for this? Other than opening up boxes and tracing white wires?
Expect a white wire voltage drop on furnace line (different breaker) is resulting in parallel path WW leakage > 6 mA thru the GFCI thru one of the 2 white wires on the GFCI output which has a > 6 mA parallel current.
I do have accurate enough meters to detect 4 mA current when no direct loads on GFCI outlet lines so at least can isolate which of the 2 white wires are involved on the load side of GFCI, but would think that type current would be >> 6 mA, possibly just capacitively coupled wire to wire, but all is NM, no multiple white wires in same conduit or anything. I have no idea if a bunch of NM all go thru the same stud holes though. The GFCI trip was not just at Furnace start, anytime it was on; Say 2 v drop on white wire to furnace, mA trip of GFCI would need 90 uF or so -- possible that motor start cap in furnace is involved? There is an 240 Vac A/C (off) that has about that value motor run cap on the compressor, probably need to check the white wire to that location also.
I'm assuming the old GFCI did not trip for say 6 mA, with age got 'more sensitive?' BTW, the old one checks ok by itself on a different individual circuit, did not measure the trip limits, but 2 kohm resistor trips it.
Am I missing anything? Any neat tricks for checking?
Whatever it is has been there for 30+ years.