Stray voltage complaint.
I am using a Fluke 345, 500 ohm shunt resistor and mechanical jumpers of different lengths.
When a neutral to earth voltage is measured on the Fluke 345, a 500 ohm resistor shunt is used to remove the phantom voltage. There have been many N-E voltages in this area over 7 volts.
This is a very rural area with sandy soil and currently in a drought condition. The POCO line is a 7.2kV single phase, solidly bonded wye system. There are many different properties involved with many fences separating the properties.
The Fluke 345 will show distortion factor ranges between 4-8%. The DF does not changes when the resistor is introduced.
The highest N-E voltages are measured from the POCO pole ground wire to the fence wire. There are many metal T fence post in the ground and many miles of fence wire in the affected area. Most fences become common as they overlap on corner post. When a high N-E voltage is measured, a jumper is installed between the pole ground and the closest fence wire. Current can be measured.
Today the leading opinion is the dry earth & the loaded single phase neutral are causing the N-E voltage. The fences have become parallel paths for neutral current to flow. After the next good rain, the N-E voltage will go away.
I have seen other causes other than dry earth.
I would like to prove the current is moving from the landowner's fence to the POCO ground wire or POCO to fence. The sine wave is 60 cycle.