I need help finding a resources regarding energized electrical work in regard to a “Finger Safe” disconnect on 415 volt buss duct. Some of the important details are.
The Neutral/ grounded conductor is not part of the 3 Pole “Finger Safe” Disconnect. It is just a lug. The disconnects are installed with the power off then reenergized and loads are connected with the power on. My question is- If the buss duct is fully energized with a load on it, does the neutral become an energized conductor due to imbalances or return path? There is high likelihood for the Neutral to short against ground while cables are being landed and torqued. By incidental touching of torque wrench against enclosure.
The Neutral/ grounded conductor is not part of the 3 Pole “Finger Safe” Disconnect. It is just a lug. The disconnects are installed with the power off then reenergized and loads are connected with the power on. My question is- If the buss duct is fully energized with a load on it, does the neutral become an energized conductor due to imbalances or return path? There is high likelihood for the Neutral to short against ground while cables are being landed and torqued. By incidental touching of torque wrench against enclosure.