kbsparky
Senior Member
- Location
- Delmarva, USA
I have a client with an elevator/electrical room that has a couple of smoke detectors mounted on the ceiling.
The ceiling is about 15 feet high, poured concrete. There are a total of nine(9) recessed cavities in this ceiling, about 18 inches deep or so. They look like mini-alcoves from the floor.
Along comes a state elevator inspector, and now he wants us to install a smoke detector inside of =each= of these recessed alcoves in the ceiling.
Aside from the logistical problems of erecting and moving scaffolding to accomplish this task, it appears that installing a flex type cable (MC?) would be an easier task than using EMT and individual conductors. Lots of bends to get in and out of each of these alcoves.
Can I install some riser type multi-conductor fire alarm cable into greenfield for this type of installation? It might simplify things a bit ...
The ceiling is about 15 feet high, poured concrete. There are a total of nine(9) recessed cavities in this ceiling, about 18 inches deep or so. They look like mini-alcoves from the floor.
Along comes a state elevator inspector, and now he wants us to install a smoke detector inside of =each= of these recessed alcoves in the ceiling.
Aside from the logistical problems of erecting and moving scaffolding to accomplish this task, it appears that installing a flex type cable (MC?) would be an easier task than using EMT and individual conductors. Lots of bends to get in and out of each of these alcoves.
Can I install some riser type multi-conductor fire alarm cable into greenfield for this type of installation? It might simplify things a bit ...