Does the closet/ room housing a fire alarm control panel need ventilation?

You have to maintain the operating environment within the limits for the fire alarm control panel's (FACP's) listing, typically under 120°F but usually suggested for less than 80°F. Someone will have to tell you if the closet can stay within limits without a fan.
 